on 25-12-2021 21:51
Hi,
Last night one of the rcd fuses on my panel kept tripping out. if i reset it it would then trip out again about 5-10 minutes later. After a process of elimination it turns out to be the Virgin Hub 3, if that is unplugged the electrics don't trip. Anyone have knowledge of this happening before? I am not an IT expert, so go easy on me!
Answered! Go to Answer
on 26-12-2021 13:34
It’s a Hub3 and the white LED shows it’s in router mode. If it had been red it would have been overheating, although it does seem to be in an enclosed space which is certainly not good for WiFi transmission. Your best option is to monitor and wait for a VM staff member to get to your post in a few days. You could try customer services on 0345 454 1111, but I think you will have a problem describing what’s going wrong.
on 25-12-2021 22:45
What hub is it? What is the colour or the LED on it?
on 25-12-2021 23:15
Hi Tudor,
Thanks for your reply. The main light on the bottom at the front is sort of white-ish (see image below).
Cheers
Mike
on 26-12-2021 13:34
It’s a Hub3 and the white LED shows it’s in router mode. If it had been red it would have been overheating, although it does seem to be in an enclosed space which is certainly not good for WiFi transmission. Your best option is to monitor and wait for a VM staff member to get to your post in a few days. You could try customer services on 0345 454 1111, but I think you will have a problem describing what’s going wrong.
on 26-12-2021 18:42
I have an engineer coming out on 29th, but if I could resolve it before then it would be useful. You might be right about it overheating, so I've taken it out and put it somewhere more open. It's odd, the last two days I've turned it back on in the morning and it's lasted about 6 hours before tripping out. After that it trips out every 5 or 6 mins after restarting it. It definitely is something to do with the router as when I leave it off nothing trips. Do you know if their supplying the Hub 5 now?
on 26-12-2021 20:00
Hi @mike_babb
The hub 5 is invitation only at present.
it won't be released fully until some time next year. it's undergoing testing which is why it's invite only.
To be honest a few people on teh forums have been put back onto the hun 3 as the hub 5 is too flaky at present.
on 26-12-2021 20:18
Hi Dave,
Many thanks for your reply. I’ll be happy to get whatever they give me, so long as it works. The poor thing put a six hour shift in earlier so now it’s having a rest until the morning.
Mike
on 27-12-2021 08:53
on 27-12-2021 09:34
Could be. I swapped the psu for a spare one I had and exactly the same thing happens, so if that is the issue I think the source of it is in the Hub 3.
on 27-12-2021 10:14
Is it an RCD or an MCB that's tripping? An RCD trips on an earth fault, an MCB trips on an excessive load.
If a different PSU still has the same symptoms, then that likely rules out a PSU fault. Whilst not impossible, it would be very unusual for a fault on the DC side of the hub to trigger an RCD, since there's no earth connection. It is similarly not impossible, but unlikely that the hub could take sufficient current to trigger an MCB, since these are normally set at a whole circuit value (typically around 20-30 amps) and the PSU's mains plug fuse would blow if more than the rated current was drawn. Plug fuse should be 3 amp, that would typically blow are around 6 amps.
So see what happens with a technician, but don't discount faulty wall socket wiring, a faulty circuit elsewhere, or a faulty circuit breaker.